What is the highest permissible height or elevation from the floor when installing an upright/pendent sprinkler (standard coverage k=5.6).
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: NFPA13
But depending on the situation, being to high, they may never activate
Do you have a specific situation you are dealing with ????
RE: NFPA13
There is no limit in the standard, however the laws of physics, as you might expect, do in fact still apply..
The amount of water that actually reaches the seat of the fire from a tall height depends on numerous factors like the size of the falling water droplet, and the characteristics of the fire's rising smoke and entrained air plume.
Also, the plume from a small fire in a tall space may not even reach the sprinklers to activate them. The plume cools as it rises, because it entrains cool ambient air on the way up, and reaches an maximum height where it is neutrally bouyant and spreads out horizontally.
All those factors mean that there is no "rule of thumb" for a maximum height, however a qualified fire protection PE could certainly assist you if there is a concern.
Real world knowledge doesn't fall out of the sky on a parachute, but rather is gained in small increments during moments of panic or curiosity.
RE: NFPA13
Does anyone know if there has been any fire testing in this area??
RE: NFPA13
RE: NFPA13
Making wood products
Making wood
Any storage of wood or wood product
How high , in what manner
RE: NFPA13
RE: NFPA13
****************************************
Fire Sprinklers Save Firefighters' Lives Too!