Service factor
Service factor
Hi All
If a motor is designed for a service factor of 1.15, can we run motor at these loads continuously
Can anybody clarify this
RE: Service factor
http
Good on ya,
Goober Dave
RE: Service factor
The most important is how long the motor will run, the overload percent is not continous rated so if you run the motor continous under this conditions the life will be very short.(Really will be a permanent overload and the motor most overheat and insulation will be deteriorated.
Example: You need a 10 HP motor, then you buy a 10 Hp motor and if the motor has a 1.15 S.F mind if you have an overload the motor could support saftely and shortly a 15 % of overload this is a security factor to allow the motor produce 11.5 HP but not longer, but if the motor Runs all the time in that conditions minds you have a design problem becuse you need really a 11.5 HP and not 10 HP motor.
Carlos
RE: Service factor
So the answer really is what the previous posters said, it depends, but don't expect it to be the same as buying a properly sized motor in any case. OEMs and design-build contractors tend to be the ones who use this, because they tend to only be concerned with the motor lasting out the warranty, which it likely will, and not being any larger (costing more) than absolutely necessary. If you do this as an end user, all you are doing is passing the problem onto your future self, or your successor.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Service factor
RE: Service factor
RE: Service factor
If you want continuous overload capability, it is recommended that you use the next size up to avoid damaging the motor's insulation and to ensure providing necessary torque.
Take it for what it's worth.
RE: Service factor
(2B)+(2B)' ?
RE: Service factor
Adding to all inputs, I like to highlight is not a good practice the continuos motor operation in Service Factor condition exceeding the rated load, due to some motors may not supply correct starting and pull-out torques and also experiment incorrect starter/overload protection operation.
Carlos