Has anyone seen a tyco attic head used in an arched ceiling/ attic???

RE: tyco attic head

Attics yes, ceilings no.

From my understanding of the Tyco Attic Sprinklers they are listed for attic spaces (combustible concealed) only.

For these spaces they are a great technology that reduces the amount of piping required by a large percentage. A single line at the peak can reduce several rows of lines and all the obstructions and headaches that follow.

RE: tyco attic head

I believe these are only listed for slopes of 4:12 up to 12:12.  All of the diagrams indicate a peaked roof and not an arched roof.

As stated above, my understanding is that they are only listed for concealed combustible spaces and not in non-concealed installations.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: tyco attic head

(OP)
Sorry was trying to say the attic roof line is arched


But a follow up question,      If the roof line is flat can you use the tyco attic head????

RE: tyco attic head

I think I missed your point entirely. No, I have not seen them used in arched roofs. Per the listing it seems the attic sprinklers are listed for flat, sloping roofs.

RE: tyco attic head

(OP)
sorry started off with one question and added

1. if the roof line is "arched" can the tyco attic head be used, or is this outside the listing??

2. if the roof line is flat can the tyco attic head be use, or is this outside the listing??

check page "7" say for the "BB3" it appears for it and any of the heads there is a minimum and maximum slop that is "REQUIRED"

http://www.tyco-fire.com/TD_TFP/TFP/TFP610_05_2008.pdf

RE: tyco attic head

For the BB heads, you must have a minimum of 4:12 pitch.  I believe that they may have expanded one of the heads to 3:12.  The AP heads can have a minimum pitch of 3:12.

Remember, if you have a flat roof and <36" of clearance, you need the Tyco CC1/CC2 sprinklers.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: tyco attic head

(OP)
travis

thank you for the confirmation, and the reminder

somewhat luckily, these are kind of big void combustible areas
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources