Steel lintels for 10" CMU

Steel lintels for 10" CMU

Steel lintels for 10" CMU

(OP)
Does anyone have recommendations for a cost-effective design for steel loose lintels for 10" CMU?  I usually use back to back angles for 8" and 12" CMU sized to be back from the outside edges.  But 10" CMU (9 5/8") presents a different situation as only 4" and 5" leg angles are produced.  Is 8" of steelwidth below a 9 5/8" CMU sufficient?

RE: Steel lintels for 10" CMU

I use exterior angles with a steel plate welded to the bottom, to make up the gap, so the outside walls of the CMU are supported on the steel and the interior of the CMU is closed from leaking its innards by the plate below.  On larger openings and odd sizes, I use a wide flange beam directly below the CMU, flange width equal-ish to the CMU width, and skip a course of CMU.

RE: Steel lintels for 10" CMU

(OP)
Any thoughts about using unequal leg angles to avoid needing the plate?  for example an L5x3 1/2 and an L4x3 1/2 (LLH) to make 9" below the 10" CMU?

RE: Steel lintels for 10" CMU

That would perhaps create an unbalanced load-carrying situation, and perhaps more difficult to attach through the CMU.Best run the numbers on it.  Part of the use of the welded plate is to keep mortar, spiders, dust, insulation, etc from falling out of the CMU through the gap, so it's practical as well as structural.

RE: Steel lintels for 10" CMU

What about a WT12 x ??
There's a bunch @ 9" wide, loading will be balanced, wide enough to keep the spiders out, etc.

RE: Steel lintels for 10" CMU

I agree with slta about the bottom plate welded to the angles.

Mike McCann
MMC Engineering

 

RE: Steel lintels for 10" CMU

W8 + plate stitch welded to the bottom flange. Soap blocks between flanges. Plate only the width of the opening.

W8 will be better unbraced, and easier for the fabricator to find.  

RE: Steel lintels for 10" CMU

For Steel Lintels in existing 240  masonry wall. Install angles toe to toe (weld tie plates to the flange and/or bolt through)

|_ _| 102x102x9.5;    Span<1200mm

|_ _| 152x102x13 LLV; Span<3600mm


For Steel Lintels in new 240 masonry block walls install angles back to back and stitch weld
_||_ 152x102x7.9 LLV; Span< 2200mm

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources