What load factor(s) is used for the design of pipe hangers supported from reinforced concrete slab per code?
Thank you
Thank you
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Pipe Load factors
RE: Pipe Load factors
RE: Pipe Load factors
RE: Pipe Load factors
But, just looking a dead and live loading, I would consider 1.2(DL + water). Since everything pipe full of water is known, i consider both as dead.
With that said, one must consider any thrust in bends etc.. as a load on the hangers also.
RE: Pipe Load factors
RE: Pipe Load factors
So for Strength Design (LRFD), both the 1.4 and 1.2 factor should be used.