Composite metal deck and slab

Composite metal deck and slab

Composite metal deck and slab

(OP)
Is WWF required/needed for temp and shrinkage in an elevated slab designed using composite deck? It is not needed for carrying load for the values in the deck manufacturers tables for composite deck (at least for Vulcraft). My situation is 1.5VL20, 5" overall tk. Thanks for the help.  

RE: Composite metal deck and slab

According to the SDI Specifications for composite steel floor deck, "Temperature and shrinkage reinforcement, consisting of welded wire fabric or reinforcing bars, shall have a minimum area of 0.00075 times the area of concrete above the deck, but shall not be less than 6x6 - W.14 x W1.4 welded wire fabric".

RE: Composite metal deck and slab

Oops! Correction: "... shall not be less than the area provided by 6x6 - W.14 x w1.4 welded wire fabric."

RE: Composite metal deck and slab

Just because you put concrete fill on the deck doesn't mean you need to reinforce it.

If the deck can carry your loads and is galvanized such that you are confident that it will be permanent, I don't see why you couldn't use plain concrete.
  

RE: Composite metal deck and slab

JLNJ,

I don't know why you're fighting against using the prescribed T&S reinforcement specified by the SDI. It's not specifically part of the code, but under what other specific set of circumstances would you deem T&S reinforcement is not required for concrete, based on your "judgement"? This is composite deck, and the concrete helps carry the load, not just the deck. Sounds like you were unaware of the requirement, and are trying to justify past designs where you did not provide reinforcement. Either that, or you don't know what composite deck is.  

RE: Composite metal deck and slab

If you do not provide reinforcement near the top of slab at the supports, slab has potential to crack due to negastive BM at the support.  And those cracks can be ugly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources