Secondary Injection for Transformer Differential Protection
Secondary Injection for Transformer Differential Protection
(OP)
ABB introduce a new standardized testing methodology for transformer differential protection relay , only using Secondary Injection current.
The standard three-phase power transformers introduce a fixed phase angle shift Θ of n*30º (n=0, 1, 2, ..., 11)
My case is first connection type (i.e. both main CTs stared inside) and my stepup transformer is YNd1d1.
Is this connection type aplicable for 3 winding transformer?
reference:
SA2008-000355 rev. -Universal Testing Method for Power Transformer Differential Protection -
Secondary Injection for Transformer Differential Protection
The standard three-phase power transformers introduce a fixed phase angle shift Θ of n*30º (n=0, 1, 2, ..., 11)
My case is first connection type (i.e. both main CTs stared inside) and my stepup transformer is YNd1d1.
Is this connection type aplicable for 3 winding transformer?
reference:
SA2008-000355 rev. -Universal Testing Method for Power Transformer Differential Protection -
Secondary Injection for Transformer Differential Protection






RE: Secondary Injection for Transformer Differential Protection
the answer is in the last page of the document (as I googled it):
By using this method it is possible to test the differential protection for an n-winding
transformer by testing in between two windings at a time. However, note that the SrMax
value shall ALWAYS be used for the base current calculations on all sides of the
protected power transformer. It is sufficient to test winding 1 side against all other
windings (one at the time) in order to verify proper operation of the relay for all operating
conditions.
Ciao
Erminio