Pole Embedment in Concrete
How do you determine the required embedment of a steel or wood pole into a concrete drilled shaft (assume unreinforced)?
See the attached sketch for scenario I am envisioning. What would be the potential failure modes?
RE: Pole Embedment in Concrete
http://i.imgur.com/wwfjF.jpg
Try this..
http://imgur.com/8XZyV
Your attachment is somewhere in cyberspace...
Dik
For an unreinforced drilled shaft the critical failure mode is likely to be the flexural capacity of the concrete at the bottom of the embedded pole. Design the embedment for that.
You can check the plain concrete section for flexure at the base of the post...
Couple of cautions... the pole or wood post should be protected against corrosion/rot at the concrete/steel/wood interface, the top of the concrete should slope away from the wood/steel to provide free drainage, the top of the concrete should be 6" or 8" above surrounding grade.
Dik
My only question is why would you want to do this?
It's just a simple pole footing and you are complicating it.
Mike McCann
MMC Engineering
(Public Domain Article)
http://imgur.com/qDCxk
Dik
Also, what about the vertical component of friction on the pole?
Assuming no significant deterioration, I use between 25 and 50 psi for shear-bond strength (depending on surface prep of the pole...25 psi for no prep, 50 for near-white grit blasting). I compute the pull-out resistance based on the surface contact area of the post/pole, then apply a safety factor to the result, usually at least 2 but not more than 4. If the pole is open at the bottom such than concrete or grout can flow into the pole, you obviously get more contact area, but perhaps not as much as around the outside. I consider that the contact area inside is never more than 1/2 the outside area.
For wood, it is a bit different. Initially there is bond to the wood, but as the wood shrinks, so does the bond. I'm not much of a fan of wood embedded in concrete or grout, so I have no real numbers to apply to this. Check with the Forest Products Lab of the USDA...they might have something. I know that you can epoxy coat the wood and get close to the steel values I gave, but I would keep that on the conservative side.
As for breakout, this is affected only by the moment at the pole's fixity. Pullout does not create a shear-cone as an embedded anchor would. It will fail in shear at the interface bond or in direct tension of the concrete annulus. Reinforce accordingly with spirals and vertical rebar.