line to line fault clearing
line to line fault clearing
(OP)
On a grounded wye primary, delta connected secondary step down transformer, could a secondary X1-X2 fault be cleared by the transformer primary H3 bayonet fuse or would the H1 fuse respond first?






RE: line to line fault clearing
Yd11 ==> H2 fuse