Underground trench derate of cables

Underground trench derate of cables

(OP)
I am installing a Trenwa trench system and am installing 4160V, 480V, 120V and 24V in the trench. This trench is going to be filled with sand once the cables are installed so the area classification will not be Div. I.
I would lke to know how to derate the cable going into the trench  or where to find the information to calculate this. I am utilizing "TC" (tray cable) as opposed to CLX.
Any suggestion or information would be appericated.

Thanks

RE: Underground trench derate of cables

If this installation is covered by the NEC, there is no derating required, by code, for the 480V, 120V or 24V cables.  If the 480 V cables are going to be heavily loaded on a continuous basis, you may choose to de-rate as an engineering judgment.

For the 4160 V, you would derate based on a Neher-McGrath calculation.  If you are buying a lot of 4160 V cable, some of the cable suppliers may be willing to do this calculation for you if provided the configuration.  I have been able to get Okonite to do this in the past.  In addition, there are commercial software programs that can calculate this derating for you, but they are not cheap.

Special "thermal" sand can be used to slightly improve the heat transfer characteristics.  

If you use TC cable for both 4160 V and LV circuits, you will need a barrier to separate the MV cable from the LV cable.  You might also verify that the TC cable is listed for burial in sand.


 

David Castor
www.cvoes.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources