Hello all,

On my site we are looking at installing silica breathers at the bottom of our transformer HV terminal boxes. We have had a few failures where water has ingresed into the terminal box and caused a flashover.

The concept is that the breather at the bottom will let any water/moisture ingress leave the terminal box as well as giving an indication that there is significant moisture present (via coulour change of the silica).

Just wondering if anyone has gone through the same process and whether they have had any pro's or cons to this.

cheers

RE: Transformer HV terminal box breathers

I don't think you are going to solve water ingress using a silica breather. It sounds like an issue with the cable box design. Are the boxes designed for indoor or outdoor use? Normal practice where I'm from with dry boxes is to leave a 10mm gap in the cork gasket on the bottom edge of the gasket as a breather hole/drain, or preferably a breather hole with an insect screen. I've never come across a silica gel breather on a cable box, though it will be interesting to hear what others say.
Regards
Marmite

RE: Transformer HV terminal box breathers

I've seen them on generator isolated phase bus termination cubicles. They are a waste of time. Either design the housing to inherently self-drain, or to not let water in in the first place).

Is the water definitely coming in from outside? PD activity produces water as polymer insulation breaks down.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Transformer HV terminal box breathers

(OP)
They are outdoor transformers but degradation over time has lead to the water ingress. Its definately water ingress as we can see the water trails.
Regular maintenance of our transformers is whats letting us down most, we are on a mite site and our HV maintenance is only reciently starting to come up to scratch.

RE: Transformer HV terminal box breathers

Suggest a pair of screened vents, top and bottom; and a heater inside the box. Water always finds its way in; this method helps it find a way back out.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources