IRC 2009 Table R404.1.2(1) requires one #4 cont. bar 12" from the top of the found. wall and one #4 bar near mid height of wall. This is for wall heights less than or equal to 8'.

My thought is that hor. bars in a foundation wall give the wall the ability to act as a grade beam to help bridge soft soils, etc. and to better distribute loads from above. This also helps crack control. But I've always thought rebar near the top and bottom of the found. wall is most effective, creating the larger d' distance (assuming that footing reinforcing and wall vertical rebar is not req'd).

Any thoughts on this specific requirement?

 

RE: IRC 2009 Residential Foundation Reinforcing

I presume it is for cracking.  Since the middle bar is in the center - it shouldn't be carrying much T load - so it helps with shear.

I generally use two at all three locations and 3 or 4 in the footing.

Little extra steel is cheap in a $M house

RE: IRC 2009 Residential Foundation Reinforcing

The wall acts as a deep beam when spanning soft spots. Doubt if it even gets past cracking moment. Rebar is for crack control. Mike is right. A little extra rebar is cheap. Owners hate lots of cracks in their walls.

RE: IRC 2009 Residential Foundation Reinforcing

I would think its to keep the vertical bars from walking during the pour....

RE: IRC 2009 Residential Foundation Reinforcing

I too use vertical bars to help place the horizontals at about 4' oc.  They seem to cut down on vertical or 45 cracking.  Also all on openings I put two bars with 45s at the corners.  That really helps.

RE: IRC 2009 Residential Foundation Reinforcing

(OP)
All good points, but the question is why a top hor. bar and middle? Wouldn't it be better top and bottom of the found. wall?

RE: IRC 2009 Residential Foundation Reinforcing

My guess is that if the footing is properly reinforced, and the wall is doweled to the footing, you can credit the footing steel?  Just a guess.  

I would call out for #4 bars 18" OC each way if I was taking responisbility for it.  But, I also get complaints from contractor.  Oh well.  

RE: IRC 2009 Residential Foundation Reinforcing

Not familiar with your IRC, but based on this requirement, I think it is useless.  Why bother to build a concrete wall without adequately reinforcing it?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources