Fault Rating of Single Phase Breaker in a 3 phase Switchboard.

Fault Rating of Single Phase Breaker in a 3 phase Switchboard.

Fault Rating of Single Phase Breaker in a 3 phase Switchboard.

(OP)
Hi All,

I'd be interested in some opinions on this:

Should a single phase circuit breaker in a 3 phase switchboard have a fault rating >= the maximum 3 phase fault at the board or the maximum single phase fault at the board.  The single phase fault (phase to neutral or phase to ground) is usually lower because the impedance of the neutral/ground return path.
I originally thought, you would only need to rate it to the lower fault level, but then considered the possiblity that a three phase fault could still occur if a shared fault involving adjacent breakers at the load side terminals was to occur.  Pretty unlikely I guess, but technically possible.  I'm now thinking the single phase brekaer should be rated to the 3 phase level.

For example, say at a 3 phase board the max. 3 phase fault level is 8kA, but the max. 1 phase fault is 5.5kA.  SHould you use a 6kA rated single phase breaker on this board? or should you use a 10kA rated breaker?  I think the latter.

Obviously this doesn't apply to a single phase switchboard, the maximum single phase fault is all you need to rate devices to.

 

RE: Fault Rating of Single Phase Breaker in a 3 phase Switchboard.

In your situation the 1-phase breaker should be rated for 3-phase fault level. I understand that the intake supply is 3-phase. A 3-phase fault downstream of the switchboard will produce higher current than 1-phase to ground (as per you figures).   

musa UKPN

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources