EC&M Short Circuit Calculation Guide wrong???
2

EC&M Short Circuit Calculation Guide wrong???

EC&M Short Circuit Calculation Guide wrong???

(OP)
Hi friends!

I recently tracked down an EC&M article discussing the calculation of short circuit calculations using the p.u.
They have the following for fault impedance calculation of:
ZFault=(Zutility+ZT1)||ZMotor1||ZMotor2=(0.0021+j0.083+0.005+j0.07)||(0.49+j13.8)||(29.8+j298)=0.166+j2.817 pu

I added the Zutility and ZT1 together in series and calculated the rest in parallel but get 0.007006 + j0.15125 pu. Am I missing a step here? Can someone point me in the right direction??

The article can be found here:
http://ecmweb.com/mag/electric_shortcircuit_calculation_methods/



Thank you in advance!
-EITengineering
 
 

RE: EC&M Short Circuit Calculation Guide wrong???

2
It seems that the reason for the discrepancy is explained in the discussion following the paper. That is, the transformer impedance must be converted to the correct base first (100MVA instead of 2MVA).

But why use such manual methods, when software is available, even freeware. See http://pp.kpnet.fi/ijl for example.

RE: EC&M Short Circuit Calculation Guide wrong???

(OP)
Thanks ijl!

Great! now my calculation comes pretty close :)

The reason I want to learn the manual calculation is so i can better understand the results and data input required for the software.

Thanks again for the help!
 

RE: EC&M Short Circuit Calculation Guide wrong???

Try to change the Rt and Xt to:

Xt = .07 * (100/2) = 3.5
Rt = 3.5/15 = .2333

With this, the resulting values will be almost the same. The EC&M article forgot to change the old pu to new pu values using new base MVA.

http://www.powerqualityworld.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources