Minimum concrete strength!!!

Minimum concrete strength!!!

Minimum concrete strength!!!

(OP)
Per ACI 318-08 Table 4.3.1, for exposure class F1, F2 and F3, min. f'c is 4500 psi. Can exterior concrete wall footings (extended below the frost depth), interior concrete footings and slab on grade (not a parking garage) be classified as F0 and specify only a min. f'c 2500 psi? Would appreciate your help.

RE: Minimum concrete strength!!!

If freeze thaw cycles do not occur and the other three exposure categories aren't applicable then you fall at the "0" level for each and can use a minimum f'c of 2,500 psi unless required to use a higher strength per 1.1.1 or 5.3.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources