Grounding requirements for Slurry Storage Basins

Grounding requirements for Slurry Storage Basins

Grounding requirements for Slurry Storage Basins

(OP)
Does anyone know the requirements in grounding Slurry Storage Basins? The slurry is composed of Oil, Water, and solids that are produced from cleaning Oil Tanks. The basin is roughly 80'L and slopes down to 10', is concrete with fixed metal handrails on the sides and removable handrail in front for trucks backup and dump. Do I need UFER grounding? Can I just clamp the handrails to a ground well that I plan to place in the 4 corners of the basin? Do I need to place a designated grounding for the truck to connect to ground onto?  

RE: Grounding requirements for Slurry Storage Basins

Why do you need to ground the Slurry Storage Basins? For lightning protection? There is an electric device in this basin to be supplied or there is an overhead electric line in the closed vicinity?

RE: Grounding requirements for Slurry Storage Basins

(OP)
The area is a Class 1 Div 2 location. A submersible slurry transfer pump, 20HP, 480V will be at the bottom of the basin and will transfer the slurry to a mixing tank. Trucks transfer oil, water slurry to and from an Oil Tank to this disposal/processing location.

RE: Grounding requirements for Slurry Storage Basins

I think the Slurry Storage Basins may be assimilated with Natural and Artificially Made Bodies of Water. NEC Art. 682 "Natural and Artificially Made Bodies of Water"
NEC art 682.33 "Equipotential Planes and Bonding of Equipotential Planes" requires :
"An equipotential plane shall be installed where required in this section to mitigate step and touch voltages at electrical equipment."
This could be made by embedded  conductors in the concrete .Using the rebar for this is a good idea using a minimum 1/2" diameter for main rebar [around] and as a connector to outdoor grounding electrode .
The main grounding rebar has to be welded [at least 1 inch length weld] where it is necessary. The foundation grounding has to be bonded to the system grounding.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources