Continuous slab rebar question in field.

Continuous slab rebar question in field.

Continuous slab rebar question in field.

(OP)
Hello guys, I have a simple question for field engineers:

How does concrete people accomplish slab saw cutting in field (such as 10'x10' slab saw cutting specified on drawing)? Do they leave rebar in slab continuous, or the rebar will actually become discontinuous?

We hope the rebar continuous, but just would like to make sure if it is really the case in field.

Many Thanks.
 

RE: Continuous slab rebar question in field.

It may seem like a dumb question but is this a slab on ground or is it suspended?

RE: Continuous slab rebar question in field.

(OP)

I am talking about a foundation slab of cause. Sorry about not clearly expressed.

RE: Continuous slab rebar question in field.

For SOGS most designers specify 1/2 or all of the bars be cut. This would probably be done before pouring. Your concrete saw may or may not clear the bar depending on clear cover and cut depth specified (its usually close - bar in top 1/3 and cut 1/4 depth).

csd72 is probably alluding to the fact that elevated slabs should not be saw cut.

RE: Continuous slab rebar question in field.

I usually don't cut bars.  There is sufficient cover to put the TUL below the blade.  If I want a joint, I discontinue rfg and use proper dowels and a proper joint...

With small ratios of reinforcing, if sawcutting is done on time, there is no need to discontinue half the bars.

Dik

RE: Continuous slab rebar question in field.

If the reinforcement is there to restrain the slab for temp and shrinkage, and the joints are there to allow T&S, it's up to you.  Depending on subgrade preparations and magnitude of live loads, you may wish to have something to maintain continuity of the slab across joints.  Allowing mesh or deformed bars to cross the joint will help maintain aggregate interlock.   Smooth, de-bonded dowels, or similar, will also reducing faulting at joints, with varying efficiency, depending on static and moving loads, and subgrade.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources