Placement of Anchor Bolts

Placement of Anchor Bolts

(OP)
I have a project where the contractor has been "floating" or "wet sticking" anchor bolts and wall dowel bars into the top of a concrete foundation.  I know that ACI 7.5.1 does not allow this for dowel bars, but I have not been able to find anything regarding requirements for placing anchor bolts.

RE: Placement of Anchor Bolts

I would think that placement of anchor bolts should be covered in the structural steel standards.  Maybe AISC rather than ACI?  But you can't rely on standards for everything...the project specifications should define acceptable practices.

RE: Placement of Anchor Bolts

It is a bad practice in any case.

RE: Placement of Anchor Bolts

The question is, do you want them to work and be in the correct position?  If so, don't allow it.  ACI 301-10 5.3.1.3 reads, in part "Position and secure in place expansion joint materials, anchors, and other embedded items."

RE: Placement of Anchor Bolts

Thanks TXS... I clearly stipulate that anchor rods are to be set by means of a template.  Wet sticking is not permitted; I suspect it has a real impact on the pullout strength of headed anchor rods.

Dik

RE: Placement of Anchor Bolts

One huge problem is that they are usually set in partially set concrete and even if set into fresh concrete, the surrounding concrete is not consolidated after placement (since doing so would move them.)

RE: Placement of Anchor Bolts

(OP)
I appreciate everyone's responses.

We do have notes that cover this in our spec but the contractor is balking a little bit and says that what he is doing is "standard practice".  He wanted to know if he could still "wet stick" and use a vibrator to consolidate, but I told him I didn't believe that "wet sticking" was even allowed by code. So I wanted to find an actual code that would back me up.

RE: Placement of Anchor Bolts

You have this backwards.  If your specifications cover it and prohibit it, then it is the contractor who needs to provide back up for his assertion that it is "standard practice".  A favorite tactic of some contractors is to say, when they are caught, that what they are doing is "standard practice" or "industry standard".  Don't fall for it.

RE: Placement of Anchor Bolts

It's not standard practice, that I'm aware of... in fact, it's frowned upon...

Dik

RE: Placement of Anchor Bolts

Try this line, 'it's standard practice for engineers to reject any work that doesn't meet our specifications so you're going to have to remove and replace'.

I've done it.

The look in response is priceless.

I say we start a campaign to make THAT standard practice.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close