synchronization: 2 questions

synchronization: 2 questions

synchronization: 2 questions

(OP)
1-Is it OK?
- bus running refers to system bus
- bus incoming refers to generator bus

2- phase-to-phase voltage synchronization is best than
phase-to-neutral voltage synchronization ?

RE: synchronization: 2 questions

1. Yes, incoming = generator is the "usual" description, but there are exceptions.

2.  I prefer Phase-Phase voltages with both running and incoming voltages derived from voltage trsnformers with grounded secondary circuits to prevent floating voltages.  Line-neutral also works.  

It is best to monitor the voltages to the synchronizer or synch scope with either voltmeters or a synch check relay with uner/over voltage elements to detect fuse or VT failure that may give false synch voltages.

Search sycnhronizing on this site. Thre have been a lot of dicsussions on the various methods pros/cons.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources