protection of diesel generator cable

protection of diesel generator cable

protection of diesel generator cable

(OP)
i have a project with 1500kVA,3.3kV diesel set, the set supplied without circuit breaker. the distance between the diesel generator and the diesel generator distribution board about 25 meters.
may i installed circuit breaker for the diesel generator and cable protection  only on the distribution board.  

RE: protection of diesel generator cable

Maybe.  It is going to depend on what particular installation codes apply.  If you provide information on the location of the project, it might help.  

 

David Castor
www.cvoes.com

RE: protection of diesel generator cable

(OP)
installation code according to IEC

RE: protection of diesel generator cable

On a machine of that size and value I'd install some form of unit protection to include both the machine and the cables to the generator breaker within the protected zone. If you're using a mid-range relay like a GE G650 then a restricted earth scheme is likely the best compromise between protection and cost. A stator differential relay would be even better, but stator diff. comes at a price and is normally seen only on much larger sets.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources