Upside down Drop cap
Folks,
I am having a situation where there are planter boxes (2m x 2m) right above columns. The slab is supporting landscaped area.
Can I thicken the slab into the planter box to get more punching shear capacity? In essence, it would be a upside down drop cap.
I have never seen one like it and not sure if it even works.
Your thoughts are appreciated.
RE: Upside down Drop cap
Sure it works, just follow the stresses. Typically some inclined rebar could hang the slab from the thicker part.
Just be sure you locate the potential cracks in the correct locations.
sickdeals,
Yes, but
- punching shear check at the face of the drop panel is different, critical perimeter is D closer to the support
-  PT effects for the change in section are reversed so they now hurt you. You wll need to drape tendons up into the upturn for them to be efficient.
Agree with rapt,
Actually even if I did disagree I wouldnt dare saying it on a topic like this. He would run rings around me atom
The main difference is not so much what happens directly ove the column as it is the implications at the perimeter of the up stand. Top reinforcement is not continuous so the critical bending point would be inside the edge not at the edge as for a downstand. Also the shear perimeter is different as rapt has stated.
I don't think your exterior critical perimeter is right.  The exterior critical perimeter would be the perimeter of the thickened portion as the crack starts at the top of slab and travels down towards the column.
I think you need a mechanism to transfer load up into the thickened top to make use of it.
It sounds to me like the thickened slab isn't required for any flexural considerations, only for shear.
So the top reinforcing runs continuous through the drop at the elevation it needs to be to work with the slab. Add a couple bars, bent at each end, in the top of the drop for temp/crack control and I think you`ll be all set.
I agree about the exterior perimeter. I think it would start at the corner/edge of the thickened slab and travel down @ a 45 degree towards the column, rather than traveling down to meet the corner of the column.
Couldn't you also look into something like stud rails to increase shear capacity without the upside down drop?
Slickdeals,
the others have it right, the shear perimiter for the drop panel starts at the corner of the drop panel back at 45/30degrees depending on the code (ACI, BS). It does not reach the column face.
I would treat the top reinforcement like you would at a step in the concrete with the reinforceemnnt over the column at minimum cover to tohe top of the drop panel. The bars crank at the end of the drop panel down into the slab and need full development into the slab past the cross-over point with the slab reinforcement. And then lap with a bar at top of slab level with a full developemnt length into the drop panel past the drop panel reinforcement to provide continuous reinforcement. Otherwise punching shear and everything else does not work and you may as well leave the drop panel out completely.
Agree with rapt, except I would run the top bars continuously through at one level, and add another mat at the top of the upstand "drop", developed as he described.  A 2 metre wide section is not enough to complicate the reinforcement by stopping and starting.
It may be easier to visualize what happens by inverting your detail.  Now you have what would occur with a column bearing on a slab, with a deepened section as the footing.
hokie,
Yes, a bit more practical your way! The bars would be just about butting together anyway!
I guess I would have concerns with this scenario in that two pours will likely be required here as opposed to the dropped condition.  That gets into making sure the interstitial surface adequately bonds the two pours.  Otherwise, you're kidding yourself.
Mike McCann
MMC Engineering
M^2,
I had a similar question previously on a pile cap. We could use vertical bars to tie the two pours together in case they are placed separately.
No, you don't need two pours.  The square form required to place the upturned section can easily be supported on the top layer of reinforcement.
Hokie:
OK.  Out of curiosity, what would you use to support the form and yet maintain concrete cover for the rebar?  Concrete standoff blocks?
Mike McCann
MMC Engineering
No, you just use bar chairs off the top mat, turned upside down.
I have seen this done but not for this level of step, also, be wary of potential compaction issues at the bottom of the step.
csd72,
He didn't say how deep the upstand was likely to be, but I took it to be only 150 or 200, and the box for that is easily supported.  Some tie wire is required to prevent the big-footed concretors from displacing it.  Yes, you have to compact under the form.
All:
Sorry for not giving a lot of information.
Grid: 8.5m x 8.5m
Loading: 18 kPa + self weight
Assumed : 300mm slab with 150mm thickening above column.
column size: 800mm x 800mm (arch preferred due to parking below)
Upstand is 1100mm high, not sure at this moment as exact dimensions are being worked out.
Slick,
can you please clarify the difference between the 150mm thickening and the 1100 upstand.
Also, have you considered the implications for future modifications? What if the owner turns around in 5 years and wants the planter boxes removed? You will not have won yourself any friends if this happens.
I think that csd made a good point about possible future movement of the planter boxes.  I, too, have seen this happen.
Although it would work, you might want to rethink this.
Mike McCann
MMC Engineering
All:
The planter boxes are irrelevant in this discussion. The deck is a landscape area. Any thickening I have above the slab will be hidden by dirt. For all intents and purposes, I don't care whether the planter boxes exist or not.
My idea started out as a thickening into the planter box. But I realized that it did not matter because of the thickening being hidden by soil above. In the sketch I sent, assume the planter boxes do not exist.
Just as important as your structural design is the waterproofing of the landscaped area.  Maybe that is not your responsibility, but you should gain some confidence that the waterproofing and protection thereof is first rate.
slickdeals,
My comment still stands. I have seen these landscape areas turned into cafes or similar at a later date. I have also seen engineers be too smart for their own good and create problems for future renovations.
These are soft requirements for sure but if you are just doing this to save the client a little money then you probably wont save them anything in the long run.
You are also introducing 4 additional corners to the waterproofing which is the greatest source of problems in these.
Maybe I understood slickdeal's building differently from you, csd72.  I thought the whole area was covered with maybe 600 mm of soil, and there are tree boxes over the columns, which would be a good place for the trees.  Maybe I had a preconceived notion because I have seen it done that way.  There has to be an allowance for kiosks, etc. on top, but that is typically included as live load.
Agree about the waterproofing.  The edges of the upstand should be tapered so there are no sharp corners.  And the waterproofing has to be protected from damage during installation of the landscaping materials.
@Hokie:
You are right about your assumption. Most of this deck is filled with 600mm soil with tree boxes over columns.
@csd72:
Good points on the waterproofing. Will certainly keep that in mind. Hokies suggestion of tapered perimeter will help.
A little bit off topic - but you don't reinforce the planter walls?
Most landscape folks around here aren't up on their concrete design & the Architect/Owner insists "It's concrete therefore it's yours to design" for site walls & sidewalks. It seems strange (to me) not designing concrete walls supported by an elevated concrete slab.
slickdeals,
Looks good to me.
St20036,
I think most of us would show this type wall in a typical detail instead of in a major structural section.  He has just referenced the walls here.
slickdals
The top bars in the drop cap need to "lap" with the top slab bars. They do not appear to have sufficient overlap to do this in your shetch. I would have them following the sloping concrete profile rather than a 90 degree crank to give a much longer "lap" and extending far enough into the slab to provide a full lap.
I hope when this was analysed for the PT effects and strength
- the drops were on the top as shown and not just on the bottom.
- the local effects around the drop for effective depth etc were separated from the calculations for the areas outside the drops.