SEL-351S
SEL-351S
SEL-351S
can I use SEL-351S for distance protection? if yes, how do I set the protection zone 1 and 2? thanks
RE: SEL-351S
No.
RE: SEL-351S
thanks, can I use sel-351s for directional over current protection?
RE: SEL-351S
Yes.  Have you even looked at the list of elements in the relay?
RE: SEL-351S
Thanks David,
have you used sel-351s for SER. I am trying to see the response of the relay to trip low frequency setting point. ie: if I set the low frequency trip at 59.0Hz I got it to trip but I was not sure at what frequency did it trip? (59.1 or 58.99) can I use SER to see the actual trip? if yes how?
thank lots,
Kun
RE: SEL-351S
The SER will tell you precisely when it tripped and when the 81 element operated, but it won't tell you what the frequency was.
The frequency is reported every 1/4 or 1/16 cycle in the standard event report.  You could trigger an event report with an 81D relay word bit.
RE: SEL-351S
If you are trying to test frequency response, you need to gradually vary the frequency rather than step changes. The relay may not respond well to a frequency step change as a step change will never happen in the real world. The relay may decide it is seeing bad data and not respond to the frequency until it is sufficiently stable.