Regular Instant Voltage drop in a large warehouse facility!

Regular Instant Voltage drop in a large warehouse facility!

Regular Instant Voltage drop in a large warehouse facility!

(OP)
I am working on a power failure issue at a big warehouse distribution facility in NY. I posted on the site a while ago regarding finding a solution for the power brownouts they have been having that caused the forklift chargers to fail. I recommended using the FLUKE 175 to record power parameters for a period of a week, the data results came back and it shows that they had one incident of a voltage drop on two phases from 277VRMS to 120VRMS, the drop was instantly and then came back to normal, this caused power failures and caused the current to spike. Other than this voltage fluctuation ranged from 275VRMS TO 288RMS max during that week and I think it is normal. I am trying to find the best and more economical solution for this matter, I called the power company before and they said that they didn't report any brownouts or power issues in that area!

Thank you ,

RE: Regular Instant Voltage drop in a large warehouse facility!

Can you correlate the voltage drop to weather?  Sometimes, a fault on the utility distribution system will cause an momentary interruption on the affected circuit but a voltage dip on all circuits connected to the utility distribution substation.  This may not be recorded by the utility or may be recorded only on the circuit that tripped.
 

RE: Regular Instant Voltage drop in a large warehouse facility!

(OP)
It keeps happening every month or two once or twice even at sunny morning day, so weather is not the problem!

RE: Regular Instant Voltage drop in a large warehouse facility!

How long were the dips? And were there any high voltage transients when they came back? Do you have any graphic representation? Or doesn't the 175 have graphics?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Regular Instant Voltage drop in a large warehouse facility!

It may seem obvious, but has anyone checked the tightness of all the connectors and cable lugs, etc.? Perhaps a shutdown should be arranged and everything from the transformer secondaries should be tightened up, possibly. It could be also a bad primary fuse or fuseholder acting up. Your self and the power company together.

Especially if it an old installation where corrosion has occurred. Any copper to aluminum connectors in the circuits?

rasevskii

RE: Regular Instant Voltage drop in a large warehouse facility!

That sounds like a bad connection spasming to me too.  Consider a thermal scan of all the panels and fuses that supply the location you monitored.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Regular Instant Voltage drop in a large warehouse facility!

Could be that the chargers are failing shorted and then clearing. If you are measuring closer to the charger than to the transformer those readings may be realistic.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Regular Instant Voltage drop in a large warehouse facility!

(OP)
It happens less frequently than I mentioned, I would say on average once every two months. If it was a bad connection I would expect it to happen once a day or couple of days, also the dip was short exactly 3 seconds on phase'A' then it went back to normal?

RE: Regular Instant Voltage drop in a large warehouse facility!

Three seconds? How often does the 175 sample?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Regular Instant Voltage drop in a large warehouse facility!

How far from the service transformer to the main panel? How far from the main panel to the sub panel? how far from the sub panel to the chargers? Where on this system are you connecting your instrument? Does your instrument have a recording function or just a hold function?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Regular Instant Voltage drop in a large warehouse facility!

You might want to rent a power quality meter that can record a waveform of the dip.  If every dip is exactly 3 seconds and the voltage dips from a steady 277V to a steady 120V, then there is something strange going on with some equipment in the plant.
 

RE: Regular Instant Voltage drop in a large warehouse facility!

I have seen this before. The reasons were found to be due to faults on any of the 11kV distribution feeders from the utility 132/11kV substation, but the dips were not of the range of 3 seconds!

When compared the date/ time of the dips recorded at customer's installation exactly co-related to the faults recorded on the utility main substation. The fault level on utility main substation was high enough and together with high impedance of transformers (as 3x 50MVA 132/11kV transformers were running parallel) a voltage dip observed upon occurance of a momentary and/or permanent fault. Those dips caused the customer's ACB's to trip to under voltage function as well.

As advised by others, please refer matter to utility and check the utility fault data against the dips at customer's installations.

musa UKPN

RE: Regular Instant Voltage drop in a large warehouse facility!

Not following you at all, mjawhary

Are you really using this Fluke 175?  http://www.fluke.com/fluke/usen/digital-multimeters/fluke-170.htm?PID=56027

Does it really record over weeks? Battery life seems to be only a few hundred hours and I see no recording possibility in the data sheets. Or do you use some other instrument?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Regular Instant Voltage drop in a large warehouse facility!

(OP)
I am using Fluke 175 and yes it measures and records all wave forms, it is a powerful instrument, I was able to view the event on the graphs. I ll check with the utility again and do some more research.
Thank you  

RE: Regular Instant Voltage drop in a large warehouse facility!

Something doesn't compute here. How fast does your 175 sample?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Regular Instant Voltage drop in a large warehouse facility!

Have you left out any numbers in the meter model number? How far are you from salt water?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Regular Instant Voltage drop in a large warehouse facility!

(OP)
Sorry I meant FLUKE 1750 not 175. I am far away from salt water.

RE: Regular Instant Voltage drop in a large warehouse facility!

OK. That's better. You really need to be more careful.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Regular Instant Voltage drop in a large warehouse facility!

One more possibility into the mix.

Large Wye Delta starters can cause this sometimes. There is a phase shift that takes place when they transition from Wye to Delta and depending on where the phase angle of the supply is at the moment of transition and the possibility of an incompete decay of the motor magnetic field, the combination can cause very severe transition spikes that are known to not only damage the motor, but cause seemingly random voltage dips and spikes in the system. The randomness stems from the combination of issues that it takes to cause this.

So to eliminate this possibility, check EVERY marge-ish motor in the warehouse, making sure you especially pay attention to any chiller compressors for the HVAC system (or refrigeration compressors if it's a cold storage warehouse). If you (or your neighbors) have absolutely no large Wye-Delta starters, then look elsewhere. But if you find one, put your recorder on that motor fpor a while.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: Regular Instant Voltage drop in a large warehouse facility!

Oh yeah, nice one Skogs!  An excellent candidate for this scenario.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Regular Instant Voltage drop in a large warehouse facility!

You probably meant Jeff.

I am the one that doesn't understand the measurements. A 'square' dip three seconds long is not normal at all. I still think that the measurements are wrong. I have asked a few times how fast that 175 (now 1750) is sampling. Perhaps every third second?

If that is so, you can have lots and lots of those dips, but sampling and dip coincides only now and then. So, the conclusions may be all wrong. There are many more of them and the duration is much shorter.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Regular Instant Voltage drop in a large warehouse facility!

The reason that I asked about salt water:
I had a customer complaining about an Automatic Transfer Switch.
There were two problems.
1 The watchman/gardener/handyman spent a lot of time sitting in a chair against the wall. From time to time the ATS would "thump". He would report the thump to the owner.
After some conversations with a utility engineer, I found out that during the summer months salt spray would build up on the insulators on the distribution lines near the beach. This time of year, the humidity would increase and the formerly bone dry salt film would absorb moisture and insulators would randomly flash over. Whenever there was a flash over, there would be a voltage dip throughout the system. The ATS was contactor based and the contactor would drop and pull back in with a thump. No damage was done. The best solution was to move the chair.

I asked about your system topology. Determining the system layout and then moving the measuring point helps to determine whether the problem is local or utility based.

Gunnar:
Measurement type      True rms (one cycle calculation by overlapping each half cycle - voltage between lines is measured for 3P3W lines and phase voltage is measured for 3P4W lines)
Displayed data      Amplitude and duration of dip or interruption
Measurement      Same as rms voltage

If it does what it says. It is a Fluke. grin
 

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources