Fire Water Pump Mechanical Test Run

Fire Water Pump Mechanical Test Run

Fire Water Pump Mechanical Test Run

(OP)
Is the use of Shop Motor acceptable for the Mechanical Test Run of Fire Water Pump purchased under NFPA 20 or the use of the Job Motor Mandatory? Thanks Guys...

RE: Fire Water Pump Mechanical Test Run

There is no requirement for a mechanical test run in NFPA 20.

NFPA 20 requires a field acceptance test:

"1-6.2 The complete unit shall be field acceptance tested for proper performance in accordance with the provisions of this this standard."

Fire pump experts, including the manufacturers and installer, typically do acceptance tests. Insurers and Authorities Having Jurisdiction are typically present as well.

Why would you want to do a mechanical test run as well as a field acceptance test?

 

RE: Fire Water Pump Mechanical Test Run

(OP)
Shop mechanical test run would be the best time for any modification in case there will be abnormalities (vibration, performance) and sufficient time is still available. If any abnormalities will be found during the field test run, then this would have much cost impact including schedule impact.

RE: Fire Water Pump Mechanical Test Run

I was thinking that it would take some effort to install a shop motor just for a field test and then repeat that work with a new motor.

I don't believe that a shop mechanical test run with a shop motor is prohibited by NFPA 20.
 

RE: Fire Water Pump Mechanical Test Run

5.5 calls for Certified shop test curves being provided, but does not state that they have to be created using the job motor.

RE: Fire Water Pump Mechanical Test Run

(OP)
Our usual practice on other pumps especially API 610 pumps is that when doing the performance test, shop motor is acceptable especially if motor overload could be a problem. However we use the job motor for mechanical runnning test.

RE: Fire Water Pump Mechanical Test Run

I believe the whole package still has to be FM approved at least in most applications by the Authorities Having Jurisdiction (saves them huge amounts in not having to hold the expertise to do it themselves).       

Note that supposedly, we cannot use any component on the system that is not the same identical one that it was approved with.

Realistically our people have fought that battle and things like hoses, filters etc are "ignored".   

Still has to pass the field certification test.   

 

RE: Fire Water Pump Mechanical Test Run

(OP)
Thank you all guys for informative comments...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources