NCMA CMU Lintel Values

NCMA CMU Lintel Values

NCMA CMU Lintel Values

(OP)
I've been designing some cmu lintels and some configurations I need are not in Table 4 of TEK 17-1B. I created a spreadsheet to design my lintels and checked it against the Table 4 values. What is strange is some Mresisting values match and others are off by a significant amount, say 15,000lb-in. The equation is so simple, I don't believe I have an error.

Has anyone verified the table values? Or does anyone have a suggestion of why my values are significantly higher?

Thanks

RE: NCMA CMU Lintel Values

Maybe the TEK values do not only check for flexural strength, but also limit the width of the cracks, or, even more likely, limit the deflection. The first will give you -when controlling design- a lower moment available for a standing amount of reinforcement, whereas the deflection control won't allow some loads permissible in strength (then some moments) be placed on the dintel due to poor deflection performance.

RE: NCMA CMU Lintel Values

Are you looking at both shear and flexure? Shear can be the controlling factor.  

RE: NCMA CMU Lintel Values

(OP)
I was speaking about the moment values listed. I know the shear
can control, but I am simply trying to match the table moment values.

thanks

RE: NCMA CMU Lintel Values

They might be using a triangular load assuming that arching action occurs. This is not a good assumption if there is a control joint beside the opening.

RE: NCMA CMU Lintel Values

Good point Steve.

Mike McCann
MMC Engineering

 

RE: NCMA CMU Lintel Values

(OP)
Forgive me guys, but Mresisting of a cmu lintel is what it is, regardless of how you assume the load is distributed from above.
Right?

RE: NCMA CMU Lintel Values

For a certain given amount of steel and grout strength, yes.  It depends on how your tables are set up.

Mike McCann
MMC Engineering

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources