ASME Boiler Code
ASME Boiler Code
ASME Boiler Code
If I install a new boiler rated for 150 psig, are two isolation valves required by the ASME boiler code or can I install a single check valve and butterfly isolation valve?  The boilers do not contain a man hole, instead they have a hand hole only.  My understanding of the code is that two forms of isolation are only required if the boiler is above 15 psig and the boiler contains a man hole.
Thanks for the help in answering this question.
RE: ASME Boiler Code
I am presuming that you are talking about the intent of PG-58.3.2 of Section I.
Two stop valves are required when two boilers are connected to a common steam header or when a single boiler is connected to a steam header having another steam source. In this case boiler(s) should have at least one manhole. For two stop valves, Manhole opening is a condition but 15 psig is not a condition.
I am sure two stop valves cannot be replaced by one check valve and one stop valve.
Please see also the following interpretation;
Interpretation: I-82-09
Question: PG-58.3.2 requires, for two or more boilers connected to a common steam header, that the connection from each boiler having a manhole be fitted with two stop valves having an ample free-blow drain between them. Does this requirement apply if neither of the two boilers has a manhole?
Reply: No
Please see another interpretation
Interpretation: I-92-90
Question: Does the presence of pressure reducing valves in a common steam header waive the requirements of PG-58.3.2 for two stop valves having an ample free blow drain between them?
Reply: No.
Please see another interpreation on subject matter;
Interpretation: I-86-12
Question: When the steam piping of a boiler is to be connected to that of an existing boiler, is this arrangement considered to be multiple boilers on a common header and therefore subject to the provisions of PG-58.3.2?
Reply: Yes.
Hope it helps a little.
Nasir
Welding Engineer
DESCON ENGINEERING LIMITED
PAKISTAN
If in the USA, please check with the local Jurisdiction or regulatory body for boilers. They have the final word about such installations.
back in the 1990's, the section I code had verbage that allowed "one non-return valve plus one stop valve". The term "non return valve" was mis-interpreted to mean a simple check valve, and severall boilers on header type systems were inadequately protected . A code and civil case ensued, and the result is the current wording that requires 2 stop valves or a dobule block + bleed.
No manhole present: the required stop valve on the boiler and the addition of a check valve per boiler will suffice.
No fight your Inspector, he or she may have a different opinion not based on the ASME Code.
now for maintenance purposes if you need to shut down a boiler to replace the only valve on the one boiler...