-Powering a 4KW laser with a generator ?
Well its one mess onto the next. The owners have a plan to install a mazak space gear in a large offsite building in a rural area. The area has a REA electric system with their very expensive load demand fees. While the building has a 45KVA 208 service its nowhere near large enough.
The proposed plan is to install a 125 KVA onan generator on site to power the laser. I have suggested at a minimum running it through a isolation transformer, beyond that Im not sure. Im sure this is a strange configuration but I would appreciate any feedback the resident experts would care to share.
RE: -Powering a 4KW laser with a generator ?
A well mapped system with careful consideration of the loads will run better than something thrown together and then patched with filters and transformers.
As for a transformer- a Y secondary with the center tap grounded seems to work best. This gives the lowest potential between phase and ground which keeps dielectric breakdown to a minimum. If your generator has a Y output, ground the center of the Y and consider using a transformer on the sensitive parts of the machine only. For example, I've found on some machines the frequency inverter for the blower is usually the only thing to go when the power gets a little dirty. Instead of putting an isolating transformer between the mains and the whole machine, I use a smaller transformer just on the inverter. This is not only cheaper but it also isolates the inverter from the machine itself as well as everything else. Some machine RF/HV sections make a little noise themselves and decoupling the inverter from this keeps it happy.
Chris Krug http://krugtech.com/
Maximum Up-time, Minimum BS
Some time ago we ran a 3Kw Rofin Slab of a large generator for around 3 weeks.
Machine didn't require a transformer so i can't hekp you there.
1 thing i can add is that it cost us around $500 per day in diesel, very exspensive.
also watch your voltage as it really goes up and down as the load comes on & off, the yaskawa invertor driving your roots blower might get a hard workout compensating the voltage changes.
I would not recommend doing it.
Besides after a few of months of chewing diesel you could probably have purchased a small HV sub station for the same amount.
TTFN
Chinese prisoner wins Nobel Peace Prize
As if that wasnt enough to cobb together, and maybe for the best. They now are considering putting in another REA system. A 480Volt 50 KVA system number 2. Again this is to duck under the load demand fees. In this configuration the res would run off the 480 50 kva utility line (system2) and the rest of the building (minor load) and cooler and vacume would run off the 208Y 50 kva system (system#1)
I know this sounds like alot of BS but the LDF's are very high, in our case 51KVA for 15minutes and 1 second equates to a 670 dollar surcharge. And yes even with a 100KVA system they still kick in at 51 KVA.
Dan - Owner
http://www.Hi-TecDesigns.com