Campus 15kV underground system

Campus 15kV underground system

Campus 15kV underground system

(OP)
In a campus 15kV underground system a 4/0 AWG bare ground wire was installed (embedded) within the cement of the duct bank surrounding the non-metallic ducts and it is terminated at each manhole ground rod/ring.  A typical feeder consists of three shielded phase conductors and an insulated ground conductor.   If there is line-to-ground fault the return fault current will divide itself among the metallic shields and ground conductor.  What is the purpose of the 4/0 ground wire, that is not bonded to the rebar within the duct bank cement?

 

RE: Campus 15kV underground system

It is serving as a grounding electrode.  Since it is embedded in the concrete, it should provide a fairly low resistance ground, even though it is not bonded to the rebar.   

David Castor
www.cvoes.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources