Harmonic Solution Idea

Harmonic Solution Idea

Harmonic Solution Idea

(OP)
We are having problems in the field with drive trips, fuses blowing,etc caused by high level 5th order harmonics on our lines. With over 1000 6 pulse vfds installed and little or no filtering on the drives, the voltage distortion is really bad.

The thought is to have half of the sites pole top power transformers rewired from delta-delta to delta-wye to create a sort of area wide 30 degree phase shift on 50% of the distribution load and hopefully cancel out that troublesome 5th.

Was wondering if anyone had tried this before and seen it work in practice.

RE: Harmonic Solution Idea

Are your problems concentrated to the LV side or the (assuming) 4160 V side?

The 30 degrees phase shift will not do much to improve the LV side situation, but it will definitely be a good thing to do for 4160 V distorsion.

So, if you have the problem on the 4160 V side - just do it. But if problems are on the LV side, find other solution.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Harmonic Solution Idea

(OP)
Problem is on the distribution (12.5KV) lines. All of the individual 480V vfds are working together to corrupt the grid PQ.
Any new drives added automatically are subjected to the harmonics.

RE: Harmonic Solution Idea

OK. Then your 30 degrees idea will work very well.

It is being done with larger drives by using double secondary windings with 30 degrees phase difference (one Y and one D winding). Sometimes even with four 15 degrees shifted windings.

As I said, just do it!

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Harmonic Solution Idea

I need to add one thing; it is often good to have one of the windings in delta. That is because the triplens need a delta winding to 'circulate' in. So, make sure you either have D/D or Y/D. Y/Y will produce lots of third, ninth voltage harmonics.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Harmonic Solution Idea

So if you rewire a 480 delta winding to wye, you'll have 831.  

RE: Harmonic Solution Idea

You may have to purchase new transformers with 277V secondary windings to get 480V wye.
A previous discussions:
 Harmonics and VFDs
thread237-205555: Harmonics and VFDs

Alternately you may be able to do some phase shifting on parts of the 12.5KV lines.  

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Harmonic Solution Idea

Oh, Bill! That thread...

Threadful, I would say smile

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources