Is GFP (ground fault protection) a requirement for 480V distribution panel in NEC world?

We have a utility transformer (12.47kV – 480V), then a 480V distribution panel, then a dry type transformer (480V – 120/208V) and then a 120/208V distribution panel.

I understand that GFP is not required at 120/208V panel. So is the GFP required at the 480V panel?
 

RE: Ground Fault Protection

NEC 215.10:

Quote:

Each feeder disconnect rated 1000 amperes or more and installed on solidly grounded wye electrical systems of more than 150 volts to ground, but not exceeding 600 volts phase-to-phase, shall be provided with ground-fault protection of equipment in accordance with the provisions of 230.95.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources