sprinkler piping in attic

sprinkler piping in attic

sprinkler piping in attic

(OP)
Hi,
I have a small commercial building (~4000 sf) with wood framed construction, a sloped roof, and attic insulation is at the ceiling.  A wet pipe sprinkler system is being installed for the building with some upright sprinkler heads in the attic.  Depending on the locations of these upright heads, it could be anywhere from a few inches above the top of the insulation to 4 or 5 feet above the insulation.

My question is during the winter months where temperature drops to about 30 degrees F, how can I protect these exposed piping from freezing?  Most of the pipes can be installed below the attic insulation, but the upright piping and sprinkler heads are exposed.  Does NFPA 13 allow tube insulation on these upright piping AND using dry type sprinkler heads?

If not tube insulation, can heating cables be used where needed?

Thanks.

RE: sprinkler piping in attic

You can either provide an antifreeze loop or you can provide dry pipe sprinklers in those areas.

RE: sprinkler piping in attic

As Stookey said, you can run a separate system with anti-freeze in the attic, or a separate dry pipe system in the attic.  

Otherwise, if possible, you have the option of dry uprights.  However, remember that they are only listed up to 48" in length.  Also, the uprights have to be installed with the deflector parallel to the roof if the slope is >2:12.  This can be challenging when supplying from below.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: sprinkler piping in attic

(OP)
So insulation on the upright piping and/or heat trace is not allowed?

RE: sprinkler piping in attic

NFPA 13, 2010 edition allows heat tracing of branch lines if you use UL listed heat tracing - prior editions did not allow heat tracing of branch lines.  Insulation alone is not adequate.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: sprinkler piping in attic

Since a fire sprinkler company has to be hired anyway, suggest it be done as soon as possible, and let them advise you on best approach

There may be other factors that cannot be known, that may affect the design

RE: sprinkler piping in attic

And heat tracing needs to be monitored.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources