Transformer Sizing

Transformer Sizing

Transformer Sizing

(OP)
Hi,

I need to size a transformer to power a variable speed drive which itself will drive a 1200 kW electric motor. Because the displacement power factor is not a really an issue, the transformer could be sized for a 1200 k VA  load. How far will distorted power factor affect the transformer sizing ? The transformer ratio is 400/690 V.
Thanks for any input.

Guardiano

RE: Transformer Sizing

If 1200kW is nominal output power and considering 98% motor efficiency, lead to 1263kW input active power. But, IM is inductive load, so have to get PF from motor datasheet; maybe at nominal power PF is about 0.9, that mean about 1400kVA input power; depending of application, if overload may occur, take care about how much / how often / duration, thermal and cooling TR specs / requirments, legal standards. I think a 1500kVA TR is much better.

RE: Transformer Sizing

Just consider the efficiencies of the supply equipment and the power factor of the load. We had a VFD fed 670 kW motor supplied by a 1000kVA trafo. The calculations included the motor PF and the trafo + motor + VFD efficiencies. A 2000 kVA will be the most pessimistic size I recommend.

RE: Transformer Sizing

iop95,

The motor PF won't be seen from the drive input, only the drive PF. Allowing for the harmonic loading on the transformer 1.5MVA likely isn't a bad estimate for size.

Why can't the drive vendor provide assistance with sizing?
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Transformer Sizing

Yes, PF motor is won't be seen from drive input; I forgot VFD in may estimation but this PF is "transfered" to TR by VFD sizing. We discuss on nominal values only, but for a practical and economical estimation have to begin with load (load maxim value, service type) and thermal specifications of all devices, environment and legal conditions. 1200kW is nominal power of motor but this value tell us that load have to be below this value; depending of real load value and conditions sizing may conduct to very different values.

RE: Transformer Sizing

1200 kW mechanical load will require more than 1200 kW electrical.  

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources