Flushing Water Mains - Scouring Velocity

Flushing Water Mains - Scouring Velocity

What velocity would I look for to achieve a proper scouring in a water main?  2.5 ft/s?  5 ft/s?

Any links?


RE: Flushing Water Mains - Scouring Velocity

The velocity required to suspend and flush out the deposits depends on particle size and specific gravity. Although most small animals are of low specific gravity (about 1), inorganic deposits may have a specific gravity of up to 3. Table 4.4 provides the volumetric flow rates required to transport loose particles of 0.2 mm diameter.

A typically flushing velocity of 3.0 to 3.5 ft/ sec will normally suffice.  

RE: Flushing Water Mains - Scouring Velocity

Of course with small water lines it is fairly easy to get the velocities necessary to scour them.  As your mains get larger, the large volume of water required to achieve the scouring velocities may be difficult to manage.

For example an 8-inch main at 3.5 fps will give you a flowrate of 548 gpm, which is fairly easy to get rid of.  For an 18-inch main, 3.5 fps will give you a flowrate of 2775 gpm, which becomes more difficult to dispose of.

It is not always practical to get scouring velocities is larger pipes and you may have to live with the fact that there may be some sediment in the pipe.  This is why it is very important that the pipes are kept as clean and free of debris as possible during construction or repair.

RE: Flushing Water Mains - Scouring Velocity

Minimum flushing velocity per AWWA C651 is 2.5 fps so 3.5 fps is a good target for public mains. There is a table in the standard that indicates flows needed for 2.5 fps and the size/number of taps needed at a pressure of 40 psi.

For private fire mains, flushing velocities may potentially need to be 10 fps or higher (about 1,560 gpm vs 400 gpm for 2.5 fps).

No direct links, but you can do a search for "AWWA C651 Flushing" and find specifications or guidance documents referencing C651 for the stated flushing requirements. For private fire lines, NFPA 24 is available for viewing if you register (free) at the NFPA site.


RE: Flushing Water Mains - Scouring Velocity

Without over engineering - 3 ft or 1 meter per second is the rule of thumb generally used.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close