Design Area - Attic Space
Design Area - Attic Space
(OP)
You will have to excuse my question if it seems simple, I am still new to fire sprinkler design.
We are sprinklering a combustible attic space in an Ordinary 1 building. The building footprint is 1690 ft2.
The sprinkler system is a preaction system, and the roof slope is larger than 1/6, so the design area is required to be 2850 ft2.
Since the attic space (after taking account of the roof slope) is less than the design area, should a portion of the floor space below the ceiling be included to meet the 2850 ft2?
The code says that you only have to go the extent of one floor if it is less than the required design area, but does this apply to attic spaces?
Thanks
We are sprinklering a combustible attic space in an Ordinary 1 building. The building footprint is 1690 ft2.
The sprinkler system is a preaction system, and the roof slope is larger than 1/6, so the design area is required to be 2850 ft2.
Since the attic space (after taking account of the roof slope) is less than the design area, should a portion of the floor space below the ceiling be included to meet the 2850 ft2?
The code says that you only have to go the extent of one floor if it is less than the required design area, but does this apply to attic spaces?
Thanks





RE: Design Area - Attic Space
Any way your calculation will either be just for attic space or the floor space.
RE: Design Area - Attic Space
That is what I figured it is supposed to be for the area. I just couldn't find anything that explicitly said so. To take it further... is there a requirement for the ceiling construction (eg fire rating) between the space and attic?
RE: Design Area - Attic Space
You will calc every head in the attic. If you are unsure of what the most demanding area is, then you would separately calculate every head at the ceiling? If I understand correctly, you would calc the combustible attic space at light hazard densities and then you would calc the ceiling sprinklers at your OH1 density.
Are you really putting a preaction system in the attic? You are going to need detection in the attic to release the preaction valve. Seems odd, but I have seen stranger things in this industry, for sure!
Travis Mack
MFP Design, LLC
www.mfpdesign.com
RE: Design Area - Attic Space
Or do you mean dry pipe???
If pre action what type of detection are you going to use in the attic to trip it???
RE: Design Area - Attic Space
RE: Design Area - Attic Space
Real world knowledge doesn't fall out of the sky on a parachute, but rather is gained in small increments during moments of panic or curiosity.
RE: Design Area - Attic Space
Why do you need to heat the attic ???
RE: Design Area - Attic Space
Why not keep it simple and do a dry pipe
Instead of adding a full blown fire alarm
And making sure you have a heat detector in every area/room that sprinkler protection is in????
Almost every system I have seen has missed detection in some area,
Let alone sticking heats in the attic
What state is this in??? Roughly how many sq ft building???
RE: Design Area - Attic Space
Real world knowledge doesn't fall out of the sky on a parachute, but rather is gained in small increments during moments of panic or curiosity.
RE: Design Area - Attic Space
But, if the single interlock system trips and there is no fire, then I have to assume it would be drained rather quickly. If there is a fire, there should not be a significant delay between valve trip and water flow due to head fusing.
Travis Mack
MFP Design, LLC
www.mfpdesign.com