California Electrical Code and Halogen Free Cable

California Electrical Code and Halogen Free Cable

California Electrical Code and Halogen Free Cable

(OP)
Does California require for Halogen Free Cable on particular cable installation?

RE: California Electrical Code and Halogen Free Cable

I don't think there is a code imposing the use a halogen free cable since this cable is more expensive and has low
mechanical properties.
Applications where corrosion potential is of particular concern include communications data centers and phone
switching stations with large amounts of expensive electronics.
The toxicity of smoke is of highest concern within enclosed spaces where means of escape by persons are limited; examples include mass transit rail cars, ships, and Offshore Oil and Gas platforms.
In existing installation where extension will be ordered if the old installation was usual cable using Halogen Free cable
does not improve the corrosive smoke content in a fire process case-not at the level as the standard requires.
There are only test standards as NFPA 262 or UL1666 but the test is done in Laboratory. Was some theoretical articles
proposing a calculation mode. I did this calculation for about 5000 halogen free cables and 10 cables pvc jacketed in a cable spreading room. The result was that the halogen content per cubical m was far from maximum permitted by standard.
I don't recommend also, halogen free cables pulled through conduits or ducts due to low mechanical properties of these cables.
 

RE: California Electrical Code and Halogen Free Cable

(OP)
Thank you for your very helpful answer

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources