I have a three core power cable and a single core ground cable, both cables are going to a motor.

I need to put a junction box for both of these cables before motor. In other words I need to put a junction box in between power supply and motor.

Now can I ground the body of the junction box with the same ground cable that is going to the motor? Or do I need to run a separate cable for grounding the body of junction box?

RE: Junction Box Grounding

It would help if you said where you were because that affects which codes apply. Perhaps I should assume that you're in the US because that's where most people who don't bother to say seem to come from, but if this was a British installation then yes you could use the cable from the supply to earth both the motor and the junction box provided you maintained the size of the earth conductor.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Junction Box Grounding

ScottyUK
Could you please state the standard confirming the use of the earth conductor for both the purpose. Cause IEC 60364-5-54 does not specifically say that it is permitted or not.

RE: Junction Box Grounding

BS 7671 would allow it as long as the earth connection to both the motor and the junction box were adequately sized. I suspect that IEC 60364 would also permit this, although it's not a standard I use because we have a national document which takes precedence. You won't find every possible installation scenario listed in the standards: you need to be able to interpret the standard.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Junction Box Grounding

(OP)
I am in USA. So is it permitted in NEC?

RE: Junction Box Grounding

Quote:

I am in USA. So is it permitted in NEC?

Not just permitted, required.

Metallic raceways and junction boxes must be bonded to the branch circuit grounding conductor. I'd cite the paragraphs, but I left  my code book behind.

RE: Junction Box Grounding

(OP)
If the metallic raceways and junction boxes carry phase and ground cables of a motor, then can the same ground cable (that is going to motor) be used to ground the raceway/junction-box?

RE: Junction Box Grounding

Yes. That's one of the reasons that it's called an equipment grounding conductor.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Junction Box Grounding

The junction box non-carrying current metallic parts have to be grounded as per NEC Art.250.148.
Also NEC permits splicing the grounding conductor at the junction box if the connectors are listed [for ground] and well
fastened in place.
See art. 250.148 Continuity and Attachment of Equipment.
Art.430.12 says:
"(E) Equipment Grounding Connections. A means for attachment of an equipment grounding conductor termination
in accordance with 250.8 shall be provided at motor terminal housings for wire-to-wire connections or fixed terminal
connections. The means for such connections shall be permitted to be located either inside or outside the motor terminal
housing."
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources