Live Load For 2nd Floor Locker Room

Live Load For 2nd Floor Locker Room

(OP)
What should the design Live Load be for a 2nd floor locker room above a manufacturing facility.  It is the only room on the 2nd level (really more of a mezzanine almost). Stairs from below are the only access. Also a reference or path of reasoning would be appreciated. Location is IL, USA

Thanks.

EIT

RE: Live Load For 2nd Floor Locker Room

2
IBC 2006 says elevated platforms are 60 psf.

If the lockers are going to be "full" of "heavy stuff and you expect a lot of people - then go to 100 psf.

But if it is just a "changing" or showering area - 60 would be enough - I think.

RE: Live Load For 2nd Floor Locker Room

(OP)
Thanks Mike that sounds reasonable.

Somehow I read over the LL in the IBC 4 times and missed that every time.

EIT

RE: Live Load For 2nd Floor Locker Room

A couple of things further here:

In ASCE 7, Table 4-1, under "Office Buildings", the first two lines set the tone for design where it says "File and computer rooms shall be designed for heavier loads based on anticipated occupancy", but does not specify the design load.  That is left up to the judgement of the engineer to be based upon the occupancy, distribution, and weight of the equipment.

Also, consider AISC 4.8.4, Special Occupancies, where it states that "Live loads of 100 psf OR LESS shall not be reduced in public assembly occupancies.  

Also in the same Table 4-1, under "Assembly Areas and Theaters", is the recommendation for 150 psf for "Stage Floors".  Considering how much acting that goes on in a locker room, you might want to consider this value too.  

 

Mike McCann
MMC Engineering

 

RE: Live Load For 2nd Floor Locker Room

The design load for compactus zones varies between 150-200 psf. I don't see the need to design zones housing personal lockers for anything more than 100psf.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources