At what elevation to place reinforcement for a 6" Slab on Grade
At what elevation should steel reinforcement be placed in a thin, say 6", slab on grade? This may seem very straightforward, but I have seen different approaches to this. I have some equipment loads on my slab on grade that are significant but not excessive. Say I have a 15' x 9' slab on grade that is 6" thick. I have turndowns all around the slab. I only need a single layer of reinforcement, running each way.
Now, I would place the steel reinforcement at the bottom of the slab, with a callout like: #4@12" O.C. BOT. EA. WAY. I also place another piece of reinforcement for the side, bottom and the "angle" of the turndown. A thin strip of the top all around the slab is also reinforced. That is how I would do it.
Even my structural software says to place it at the bottom.
Now, I have seen many people place the reinforcement at the TOP of the slab, with hooks at both ends that go into the turndowns, and leave the bottom of the slab, and the bottom and the "angle" of the turndown unreinforced.
There are some people who even place the reinforcement in the middle (i.e. Between the top and bottom) of the slab.
Where should the reinforcement rightly be placed? Does the fact that it is a slab on grade make any difference? That is, soil pressure acting upwards against the slab. Your comments and feedback, please.
RE: At what elevation to place reinforcement for a 6" Slab on Grade
Mike McCann
MMC Engineering
In my opinion it is a complete judgment call. Because it is only 6", your loads must not be extreeme and the reinforcement should be for temp and shrinkage & crack control, not bending.
If the reinforcement is for bending, then you must meet the clearance requirements set forth for in ACI. And if it is a slab on earth, you need 3" clear.
Also, it is always a good practice to call out for vapor barrier between the ground and the concrete. This will help with clearance issue also.
This particular slab your looking at (15'x9')is small, but the aspect ratio is not good (ratio of length-to-width). I usually limit the aspect ratio to 1.5; yours' is 1.67. I suggest a 1/8"x1 1/2" sawcut at the middle of the 15' length, although the turndowns will help prevent cracking as well.
Dik
Reinforcement in slabs on ground are not designed for flexure unless you are complying with ACI 318. The posts above are correct that the section is designed as unreinforced and the steel is for T&S, to control the width and distribution of cracks.
In general, the deeper the steel, the deeper the cracks. But, shallower steel is subject to greater moisture, oxygen, and chemical exposure (where it is exposed to these.) The goal is to put the reinforcement deep enough to maintain protective cover and shallow enough to provide crack control at the top surface. Deeper is not better.
If you intend for the slab to act as a flexural element, as in a mat or raft foundation, design it to ACI 318.
For your protection as the design professional, specify the middle third of the slab...don't count on it being placed there, but if you don't have inspection responsibility at least that covers your liability.
The Boussinesq approach or FEM can be used to estimate the local bending in such situation.