We have a 50 HP motor at 480 v that is serviced through a 100 amp CB and VFD controlled.  It runs a large fan that exhausts fumes from one department into a Regenerative Thermal Oxidizer to "cook" off the fumes before they are released to the atmosphere. I got a call from the second shift supervison that the fan had shut down because the breaker had tripped there was no damage to the motor or anywhere in the electrical pathway to the motor. Power is generated here locally in town, I suggested they had a low voltage condition causing the breaker to trip, they denied it.  Am I correct in my assumption?

RE: 100 amp breaker tripped

I respectfully submit that you haven't provided enough information to allow a substantiated conclusion.   

RE: 100 amp breaker tripped

Depends on how he determined the was "no damage", any actual testing done?  

RE: 100 amp breaker tripped

It seems to me you have a lot more investigation to do before you can make any realistic assessment of what happened.  You say the breaker tripped.  Does the VFD have any diagnostics or logging that you can review?  Why did the VFD not take the motor offline, and instead it was the CB?

RE: 100 amp breaker tripped

(OP)
There was no faults to ground in the conductors to the motor, the breaker reset with no problem and the motor ran perfectly drawing 33 amps.

RE: 100 amp breaker tripped

(OP)
"Why did the VFD not take the motor offline, and instead it was the CB?"  
That's what I'm trying to find out

 
 
 

RE: 100 amp breaker tripped

Look for loose connections and/or signs of heating on the breaker. The most probable cause is local heating of the breaker. This may be a loose connection of the cables, the bus connections or possible internal deterioration that is causing heating.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources