Local Flange Failure
I am trying determine the flange capacity for an I-beam with a traveling trolly hoist / crane?
This is a 4 point load that will be applied from each of the trolly wheels.  The capacity of the trolly crane is 4,000 lbs and is hanging from a W8x15 wide flange beam.
Can you please help me determine the capacity of the flange (for local failure).
Thank you.
RE: Local Flange Failure
Thank you very much!
I'd use both checks
delagin,
   I noticed in your spread sheet the allowable deflections for the simple span of a monorail is listed at L/450.
In CMAA the allowable deflections are listed at L/600 in section 3.5.5.1.
Am I missing something?  Thanks.
engpes
I agree that it should be L/600
I use L/450 for cantilevers and jib arms.
This is one of Tomanovich's spreadsheets.
Maybe he could be contacted?
our standard use L/450 for monorail longer than 46 feet. i havent done any research where it came from. have you checked AISC 9th editon?
yes, tomanovich will respond if you email him. but obviously i wont put his email here.