ESFR OK For Non Storage Locations FM Says YES!! NFPA?????

ESFR OK For Non Storage Locations FM Says YES!! NFPA?????

ESFR OK For Non Storage Locations FM Says YES!! NFPA?????

(OP)

FM Data Sheet 3-26 FIRE PROTECTION WATER DEMAND FOR NONSTORAGE SPRINKLERED PROPERTIES 7/2011 ED


2.1.1.6 For new or existing Nonstorage occupancies, it is acceptable to use storage sprinklers to protect all
areas of mixed storage and manufacturing, and Nonstorage. Determine the water demand design requirements and evaluate obstructions based on the applicable occupancy-specific storage data sheet.

NFPA 13 2010 says this, yea I know says nothing about non-storage, but this all I can find. Ordinary hazard storage and mics storage has Ord Grp. 1 & 2 designs.

12.6.7 CMSA and ESFR sprinklers shall be permitted to protect
ordinary hazard storage of Class I through Class IV commodities,
plastic commodities, miscellaneous storage, and
other storage as specified in Chapter 12 through Chapter 20
or by other NFPA standards.

So if I have an extra hazard occupancy as per NFPA can I use an ESFR system? Say an injection molding operation with hydraulic fluid?? Looks like FM says yes and NFPA No????

We see this when the spec building is built and ESFR is installed and a non-storage occupancy moves in. What would you do as the AHJ??

 

****************************************
Fire Sprinklers Save Firefighters' Lives Too!


 

RE: ESFR OK For Non Storage Locations FM Says YES!! NFPA?????

Would require system to be check , if it met hazard going in, before answering along with checking listing on actual head used

RE: ESFR OK For Non Storage Locations FM Says YES!! NFPA?????

I would permit it. FMDS are prima facia evidence of compliance in the International Fire Code.

RE: ESFR OK For Non Storage Locations FM Says YES!! NFPA?????

(OP)
I have a concern in a hydraulic oil fire (as in an injection molding machine) the fire can set off too may ESFR heads since the fire is not going to be controlled or extinguished since it is a 3 dimensional fire. If we had auto shut off of the hydraulic pump say via a water flow switch then maybe. Also what about a flammable liq. operation, say spray painting or dipping, again are we going to get fire control to reduce heat output??

****************************************
Fire Sprinklers Save Firefighters' Lives Too!


 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources