NFPA 557 - Fire Loads Formulae
NFPA 557 - Fire Loads Formulae
(OP)
Hi guys,
I'm doing a bit of research on the new NFPA 557 standard for the determination of fire loads in compartments, which is draft and available next year.
I evaluated five compartments types for a range of occupancies and have found that the design fire load density outputted from NFPA 557 formula can often be up to 5 times the average compartmental fire load density? Can anyone help me as it seems exceptionally high?!
Would appreciate any help!
I'm doing a bit of research on the new NFPA 557 standard for the determination of fire loads in compartments, which is draft and available next year.
I evaluated five compartments types for a range of occupancies and have found that the design fire load density outputted from NFPA 557 formula can often be up to 5 times the average compartmental fire load density? Can anyone help me as it seems exceptionally high?!
Would appreciate any help!





RE: NFPA 557 - Fire Loads Formulae
NFPA 557 is a new standard and it's intended to assist the design community and code officials in establishing fuel loads for determining models that will evaluate fire behavior. Dr. Craig Beyler with Hughes Associates has helpful presentation on the goals and problems the technical committee faces:
http://www
RE: NFPA 557 - Fire Loads Formulae
RE: NFPA 557 - Fire Loads Formulae
RE: NFPA 557 - Fire Loads Formulae