Grid modeling with CDEGS
I am using Malz in Cdegs to analyse and model the grid of a substation.Does any one know how I can find the induced voltage on a metal pipe 50 meters below my grid and ensure that the pipe will not be dangerous in remote?
RE: Grid modeling with CDEGS
There is an option to model this pipe as another conductor which could be former by the materials (steel outside) and something else inside.
For each one you may specify all the characteristics.
After that, you include it in the soil layer corresponding to the 50 m you mentioned.
There are some informations about this in the website of the software developer that may be usefull to you.
could you please guide me to the section of MALZ which enables me to have this option?
Not sure what you are ultimately trying to accomplish here, but if you're trying to look at just induced voltage, I don't think that Malz is the right module. MALZ won't calculate induction for you. You would need to go to HiFREQ for that.
My recommendation would be to call SES. They have been extremely helpful for me in the past trying to resolve issues such as this.