Volt drop from transfo to shed
2

Volt drop from transfo to shed

Volt drop from transfo to shed

(OP)
Hi
Could you please correct me if i am wrong?

I have this situation: To supply a shed 1.3 km away from a distribution transformer (22 kV/415V - three phase)on 230V, load = 1kW. 415 kV cable used = 70 mm2 - three phase. V/A/km of 70 mm2 cable = 0.87.

Volt drop up to shed = 0.87 x 1.3 km x 4.4 A =  5 V  ??

Am i doing this right?

Thanks for reading this and pointing out errors.

RE: Volt drop from transfo to shed

1 kW delivered at 415V is just 1.4 amperes!
If you have used a 70mm2 wire, it's a big wire! (equiv. to 2/0)
You mentioned 12kV/415V and you also mentioned 230V, which is which?
If you are supplying 1 kW on a 415V, three-phase line, your Vd at end-of-line will not even exceed 0.5 volt!

RE: Volt drop from transfo to shed

Assuming the 22/0.415kV transformer is a normal star-wound type and you're taking a line and neutral supply from it then yes, your calcs look reasonable. You might want to consider load power factor, unless this is a heater or tungsten light at the far end. If it is a motor load then also consider the starting current, which will be about 6x the normal running current.

That cable you propose is quite generously sized in these days of high copper prices. smile
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Volt drop from transfo to shed

(OP)
Ah yes thx :P

They are tungsten lights at the far end and the 70 mm2 cable is Aluminium ..

Mistake: 415 V instead of 415kV in original post ..ack

Phew .. just started working as an engineer :| Takes a lot of focus

Thx for the support! cheers

RE: Volt drop from transfo to shed

(OP)
Oops, Burnt2x .. i mean i have to supply the  shed with 1 phase power supply only (230 V : PHASE-NEUTRAL) ..

If you have more questions, write it , perhaps i am missing something

RE: Volt drop from transfo to shed

Since this is just 1 phase, you will have a voltage drop in both the phase and the neutral conductor.   

RE: Volt drop from transfo to shed

For the record only the 06/1 kV 3*70 sqr.mm AL conductor cable is R+j*X
where R=0.443 ohm/km [20oC,d.c.] X=0.12 ohm/km [PVC insulated 60hz] As skin effect and proximity effect for 70 sqr.mm AL conductor is about 1.008 may be neglected. Also if the cable is laid in underground the temperature rise will be not more than 1-2 degrees C so could be neglected. Then the resistance will remain 0.443 ohm/km[according
to IEC 60228].
The resistance of the tungsten lights is 230^2/1000=52.9 ohm.
The current flowing through the 2 conductor of 3*70 sqr.mm AL-live and neutral- and the resistance of the tungsten lights is :
I=415/SQRT(3)/(2*1.3*0.443+52.9)=4.433 A
The Net voltage possible drops to 400 V[ instead of 415 V] that means the source end voltage will be 400/sqrt(3)=231 V.
I=231/(2*1.3*0.443+52.9)=4.27A [if you neglect the cable reactance] and if you don't you'll get:
I=4.27-j*0.0247 A so you may neglect the reactive part.
As we know the tungsten light luminosity will support very well a drop voltage of 5% that means even at 230*.95=218.5 will be o.k. and usually 220 V is still good.
Now we can neglect the cable reactance and calculate the voltage drop [ as actually was done]:
DV=2*0.443*1.3*4.27=4.9 V So the worst case the tungsten light supply voltage will be:231-4.9 =226.1 V.
But if you'll take 3*50 you'll get 224 V still good!
 

RE: Volt drop from transfo to shed

(OP)
wow, thanks very much .. very informative!

RE: Volt drop from transfo to shed

(OP)
Another thing .. voltage drop in the neutral conductor stands too? as mentioned by bacon4life .. it would be 4.9*2 = 9.8V?

RE: Volt drop from transfo to shed

bacon4life is right.If you'll take the maximum resistance for a stranded class 2 conductor according to IEC 60228 is only 0.443 ohm/km [it is not 0.87 ohm/km as you noted in o.p.] you'll get
only 4.9 [two conductors live and neutral].
 

RE: Volt drop from transfo to shed

What is V/A/km noted in some of the cable catalogues it is the voltage drop for a three phase cable,
load pf=0.8 and conductor temperature maximum admissible[for PVC=70oC  for XLPE =90oC]cosfi=pf=0.8 sinfi=sqrt(1-pf^2)=0.6
Vdrop=I*(R*cosfi+X*sinfi)*SQRT(3) [V/km]  I[A] R[ohm/km] X[ohm/km]
or Vdrop/I=(R*cosfi+X*sinfi)*SQRT(3)
In your case R=0.443*(1+.00403*70)=0.568 ohm/km  X=0.09  ohm/km [for XLPE insulation]
V/A/km=sqrt(3)*(0.568*.8+0.09*.6)=0.88 ohm/km.
But your pf [cosfi] =1 sinfi=0, you don't need sqrt (3) as you system is single phase, so you need only R for ambient [20oC] as 4.5 A even in underground cable is not able to rise the temperature more then 1-2 degrees then R=0.443 ohm/km.

 

RE: Volt drop from transfo to shed

(OP)
thanks everyone for prompt reply and explanation!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources