kAIC rating
kAIC rating
(OP)
Does anybody know that if the kAIC rating of a transfer-switch is 35kA at 480V, what will be the kAIC rating at 208V?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: kAIC rating
RE: kAIC rating
If the transfer switch mechanism does not use circuit breakers, it does not have a "kAIC" rating on it. The "IC" means "Interrupting Capacity" and if the devices are not fault interrupting devices, such as circuit breakers, then they cannot have a kAIC rating. If someone is telling you otherwise, they are mistaken.
If this is a MANUAL transfer switch, i.e. a double throw safety switch or a set of interlocked rotary switches, and there is a set of fuses ahead of each side of the switches, then the fuses will have kAIC ratings at the various voltages. But technically, the switch itself does not have the rating, the fuses do and the switch has a "withstand" rating, now also known as an SCCR (Short Circuit Current Rating).
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: kAIC rating
http://a
This is a service entrance type transfer switch, so it has a circuit breaker as well as a switch. The non-service-entrance type transfer switches don't have a circuit breaker (they only have the switch).
I think if I need to put a non-service-entrance type transfer switch; then I will have to put a separate upstream circuit breaker (in between utility and transfer switch).
Is it correct?
RE: kAIC rating
It appears that they use Sq. D. circuit breakers, so you can look up the AIC ratings of those at 240V, but I think I saw that specific info in the brochure anyway.
If you use your own circuit breaker, you will need to know the withstand (or SCCR) rating of the switch when used with that SPECIFIC breaker. If you use something that their switch has not been tested with, then you will need to limit the fault current to whatever level they have WITHOUT a breaker, which appears to be very low.
I would use the version with the breaker and listing already done if I were you, rolling your own has become a major headache now with inspectors.