Foundation Design for Picnic Shelter on organic silt?
hydroponder (Civil/Environmental)
22 Aug 11 10:18
I am charged with designing the foundation for a 320 square foot picnic shelter with 4 to 6 structural columns on a slab-on-grade floor.  Unfortunately, we completed two soil borings on site last week and the borings show organic silt the entire depth of the borings, to 35 feet.  Blow counts range from weight of hammer to 1, with water at about 2 feet below grade.  I was thinking of screw piles below each column, but without knowing how deep the bearing soils are, this seems a bit risky.  I guess the other option would be a structural floating slab.  Any other ideas?  Thanks.
FixedEarth (Geotechnical)
22 Aug 11 14:02
Would drilled piers work given the cohesive soils and isolated columns?
apsix (Structural)
23 Aug 11 21:41
I'd look at the floating mat/raft if the structure isn't too heavy; no masonry I hope.
EBSEngineering (Structural)
6 Sep 11 11:49
Get a deeper boring.  If there is no idication where good soil is, how can one make a guess on a foundation type.  Helical piles are certainly a good answer, but in order to get an accurate cost from a contractor, he is going to need to know how deep to go.  Helical piers can be battered if necessary if worried about lateral loads.
hokie66 (Structural)
6 Sep 11 16:39
Bored piers and deeper borings sound like overkill for a picnic shelter.  I agree with apsix.  Let it float, and make it flexible.
oldestguy (Geotechnical)
26 Sep 11 20:42
I'd let it float, but make it rigid.   I sometimes find that a rough rule-of thumb- for things like this is to tell the structural engineer to assume any square area, such as maybe 6 x 6' as not having any support, and then assign a limiting bearing value of maybe a few hundred pounds per sq. ft. at the edge of that zone.  For larger buildings I have used 10 x 10' as a recommendation and 1,000 psf, but here I think you can reduce those.
Try to avoid any grade raising as that, not the structure, will cause you grief.
If you can, remove say 3 or 4 feet from the site and beyond about 5 ft., backfill with compacted granular material as a means to help spireas out uneven loading from the slab.  Also, that minimizes problems from frost heave.
26 Sep 11 22:18
I agree oldestguy.  I reread my post, and I was talking about the superstructure as being flexible, i.e. no masonry.  The footing/slab should be rigid.
dik (Structural)
26 Sep 11 22:32
Don't know your climate, but in cold weather organic silt can move a bunch... probably the worst thing to build on... Need to use a low bearing pressure, accommodate a large deformation and also, may have to accommodate serious frost heave... maybe a foot or so... You have your job cut out... best find a better site.
Dik
apsix (Structural)
27 Sep 11 3:18
I've got to admit that I don't consider frost heave; it's just not an issue where I live.
27 Sep 11 8:27
I'm in Minnesota, so frost heaving is definitely an issue.  I ended up recommending screw piles (helical piles) below each column and also recommended completing an additional boring to determine the depth of bearing soils.  Further, I recommended that horizontal grade beams be used for lateral support if a structural slab was not to be used.  This seems like overkill for a picnic shelter, but I just don't think any other option will be adequate.
dicksewerrat (Civil/Environmental)
3 Oct 11 19:48
How much money is the owner willing to spend?
Richard A. Cornelius, P.E.
WWW.amlinereast.com
kevinindenver (Mechanical)
4 Oct 11 3:03
This would seem to be a perfect application for a Pin Foundation:
http://pinfoundations.com/boardwalks.htm
Looks like they have experience with wetlands.