Civil detail & clearances for 160kVA Trafo

Civil detail & clearances for 160kVA Trafo

Civil detail & clearances for 160kVA Trafo

(OP)
Dear Friends, I have a step-up transformer of 415/11000V, 160kVA. Can anybody provide me information on civil details? I basically need the height of foundation from FGL & how much clearance is required on all the 4 sides of transformer. Also I need to install a DG set (160kVA, 415V) in periphery of said transformer , so what distance is required to be maintained between transformer fence & DG set? Does 160kVA transformer require oil containment pit?

RE: Civil detail & clearances for 160kVA Trafo

Hi GadreP,

generally, the main objective that shall be concidered is fire security requirements. I guess that trafo is oil filled, right?

You must determine oil containment volume (oil m3 -from vendor), distances from nearest objects (fire separation), clearances on HV/LV side (voltage separation), any access road (on rails, or on the platform).
 
For fire distances from other objects NFPA850 chapter 5 is good reference.
For distances IEC 60071, Annex A, Table A.1 can be referred. But this is for HV, I do not remember if for MV also. Check it out.

regards
qqitek

RE: Civil detail & clearances for 160kVA Trafo

Following the qqtek recommendations NFPA-850 seems to be suitable.
nevertheless the standard is not recommended for general purpose but:
NFPA 850, Recommended Practice for Fire Protection for Electric Generating Plants
and High Voltage Direct Current Converter Stations,
Your transformer is filled [usually] with approx. 250 l [far from 1890 l] so NFPA-850 ch. 5.2.4.3 does not require
a fire wall to be provided for outdoor installation but if it is indoor installation you have to provide 3 hour fire resistant wall.
In connection with spilled oil evacuation ch.5.6 Drainage could be an indication.
I don't think IEC 60071 INSULATION CO-ORDINATION would add here something.
Annex A "Clearances in air to assure a specified impulse withstand voltage installation"
It covers three-phase systems with nominal voltages above 1 kV.
I think NFPA-70 [NEC] art 420.26 for indoor installation and 420.27 for outdoor installation is more suitable for a general purpose transformer.
You may also take a look of National Grid Specification [for bid]:
http://www.nationalgridus.com/niagaramohawk/non_html/constr_esb754759.pdf
 

RE: Civil detail & clearances for 160kVA Trafo

Some of the details desired are given in IEC 61936-1(ed2.0) 2010-08.Power Installations exceeding 1 kV AC Part 1 Common Rules
Transformer installation rules are given in clauses 4,5,8 and 6.2.2

Clearance on all sides for 11 kV- 3 metres
Clearance between fence and DG set - 1.5 metres
OIl pit requirement varies country to country.For this size of trf,it is not provided.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources