I would like to request information as to what a (3 x 5) AWG copper conductor equals to in mm2?

RE: (3 x 5) AWG???

I don't even know what a 3 x 5 is in AWG. Neither #3 nor #5 is a standard building cable size. It may be a special 3 conductor #5 AWG cable or assembly. Or maybe not. Can you give us any more information? Where do you see this number? What industry is this for?
 

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: (3 x 5) AWG???

Note that the #1/0 equivalent is approximate.  #1/0 is 53.49 mm².
Also note that copperweld is mostly steel and doesn't have near the conductivity of copper.

RE: (3 x 5) AWG???

(OP)
It is also a little absurd that our client standards specified this size for grounding grid, structural, power transformer, cable tray grounding conductor. Normally we use around 4/0 AWG.

The power system is low resistance on the primary and secondary distribution and HRG on the LV...is this the reason hwy they may have specified this smaller size? Comments everyone?

To make it more interesting, the associated earth-return path or equipment bonding conductors are bigger size.

RE: (3 x 5) AWG???

Thanks for the information, Thepunisher.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: (3 x 5) AWG???

If the copperweld is adequate for the maximum fault current, then it is OK.  Usually, #4/0 copper is not needed for current, but is used for durability.  Copperweld is pretty durable and has the advantage of not being worth stealing.  I've seen it used for ground grids, but it would be a pain in the a** to use for general ground connections because it is so stiff.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources