Piping network heat loss
2

Piping network heat loss

Piping network heat loss

(OP)
Dear All,

Is it worth it to consider downsizing the piping network to solve heat loss issue?

As we know, smaller surface area should has smaller heat loss

RE: Piping network heat loss

It is certainly worth considering, but the size of the piping is linked to its fluid carrying capacity and that is likely to be the controlling factor.

Katmar Software - Engineering & Risk Analysis Software
http://katmarsoftware.com

"An undefined problem has an infinite number of solutions"

RE: Piping network heat loss

Probably true.  Cheaper to add insulation diameter than subtract pipe diameter.

Regards,

SNORGY.

RE: Piping network heat loss

Hypothetically, a smaller pipe has a larger heat loss impact than a larger pipe.  

Consider the fact that the ratio of pipe's circumference to crossectional area is 2/r; the same ratio as applied to volumes is why babies lose heat faster than adults.

Additionally, smaller diameter pipe means that maintaining the same mass flow will require higher fluid velocities, which means increased pressures, possibly, as well as potentially increased pipewall erosion problems.

TTFN

FAQ731-376: Eng-Tips.com Forum Policies
Chinese prisoner wins Nobel Peace Prize

RE: Piping network heat loss

Adding insulation is typically your best bet.  Changing pipe size can have unintended consequence as others have pointed out.  Reminds me of the guy who piped his house water at 3/4" to save pressure... had to wait (0.75 / 0.5)^2 times longer for his shower to get hot.

Main point I wanted to make is to be cautious if you are insulating small pipe... insulating can increase the heat loss!  Increased surface area can more than make up for increased insulation.  Limit is set by dividing k by h.   {W/(m °C)} / {W/(m^2 °C)} = m.   k/h = critical radius.  If you are under the critical radius then you increase heat loss.

RE: Piping network heat loss

(OP)
thank you all for the responses

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources