We use time synchronising of the relays via DNP3 protocol as most of our IEDs are connected via DNP3 over ethernet LAN.I am told that this method of time synchronising is not very accurate(+/- 10 ms?) and bit non deterministic depending on network traffic.I would like to hear your views on pros and cons of time synchronising of IEDs via DNP3 protocol versus via IRIG B signal.
Regards,

RE: Time synchronisation of IEDs

I suppose it depends on what accuracy your are looking for.  For protection, I have only seen IRIG.  I recently did a project where the metering was via DNP via ethernet.  There were issues with the DNP meters only refereshing once per 24hr and the two meters would loose about two seconds between themselves.  We had to fiddle around in order to get DNP to sync every second.

In my opinion IRIG is a better and simpler approach.  You connect to the source and it works.  I understand having to run coax along with the cat5 is more wiring, but there is not much to screw up in the coax(rg-58) connections.

RE: Time synchronisation of IEDs

"but there is not much to screw up in the coax(rg-58) connections."

...or so you'd think.  I've seen multiple installers struggle with crimping the terminals onto the coax cable!

RE: Time synchronisation of IEDs

(OP)
What is the best accuracy and resolution achievable via DNP3 protocol? I am looking to achieve an accuracy of +/- 1mS  

RE: Time synchronisation of IEDs

IRIG-B, no other option seems to make sense as I see it.

RE: Time synchronisation of IEDs

We've used DNP for time synch in situations where the device had no IRIG capability.  I think the resolution was around 10 ms or so.  

For 1 ms accuracy, I think you will have to go with IRIG.  If the device has an IRIG input, it would be an easy decision for me.  The cost of the GPS time clocks gets lower every day it seems.  
 

David Castor
www.cvoes.com

RE: Time synchronisation of IEDs

"The cost of the GPS time clocks gets lower every day it seems."
  
With the cost of labor escalating, we have determined it is cheaper to add a GPS clock at each of the elelctrical rooms in the plant than to pull, terminate, and test the IRIG Coax all over the plant.

DNP does not work well for synchronizing event recorder clocks in protective relays.  It is better than nothing but gives errors when comparing event reports. During a plant trip the communications links can get busy and add additional delay errors to event records. What's the hold saying:

"A man with two watches never knows what time it is."
 

RE: Time synchronisation of IEDs

DNP works well when "close" is several milliseconds.

When you need tighter synchronicity, IRIG is the way to go.

And seriously, the cost of IRIG receivers is dropping fast, so they're not a major installation cost any more, more like a rounding error in the cost of a decent substation.

old field guy

RE: Time synchronisation of IEDs

Yep, today price of GPS is nothing.
 

RE: Time synchronisation of IEDs

We usually use IRIG-B, however, all our new IEDs in the substation yard are using fiber back to the control room, so we are left with using DNP to time sync them.  

RE: Time synchronisation of IEDs

Just curious... what is an IED ?  

=====================================
(2B)+(2B)'  ?

RE: Time synchronisation of IEDs

Intelligent Electronic Devices = protective terminals. smile  

RE: Time synchronisation of IEDs

Thanks slavag.  

Good to know.  That way I won't duck for cover if someone tells me there's an IED when touring a substation.

=====================================
(2B)+(2B)'  ?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources